    Hi Guy, 

    In Modbus, often the first digits are assumed because of the function code. For example, function code 3, read holding registers, always start with 4xxxx. So, the 4 may be assumed by the function code used. If that's the case, entering the address as 57 may work, but entering the address as 40057 won't.

    The offset is due to the fact that register addresses start at 1 and memory addresses start at 0. Hopefully this helps to explain the weirdness a little. 

    How are you entering the addresses into the Netbiter? Are you using a template? Can you share a screenshot?

    Best Regards, 

    Kyle

    0
  • Guy Farley

    Hiya. Thank you for the prompt reply! 

    I've attached pictures of Beijer config. Most of the alarm sides work, but the live data does not. Sea temp, wind speed etc. Also the Boiler On/Off and Flame status has stopped working. Engine heaters and feedback however work. 

    All working when on the HMI 

     