ABC4091 - Siemens S7-300 [profibus] with S7-1200 [profinet]

已回答

评论

2 条评论

  • 正式评论
    ALK

    Hello,

    I apologize for the late reply.

    Since you don't have a config or param error on the PROFIBUS side, my best guess is that you might have assigned GSD module addresses too high to still lie within the PLC's process image.  This is a typical S7-300 peculiarity in that address ranges above a certain threshold must be addressed differently from within your PLC program (periphery instead of process image).

    So try to attribute PLC addresses as low as possible and see if you'll be able to exchange data with the Anybus gateway.

  • djoneddd

    Hi ALK,

    Thank you for your recomendation,
    After i change the address, it's working properly now

    Best Regards,

    Joned