Anybus X-gateway – EtherNet/IP Adapter (AB7668-F)

Comments

1 comment

  • Official comment
    Siobhan Chapman

    This was answered in a support ticket so to complete this post I am copying the answers here:

    1. If a device on the Scanner side loses communication or is powered off, how does the gateway handle this? Does it zero out the bytes, freeze the last value, or signal a fault to the PLC?

    • In Anybus Configuration Manager - X-gateway, you can configure the behaviour with the "Offline option" setting for the scanner interface. You can either clear the data (setting all values to 0) or freeze it (retaining until connection is reestablished). If you have the statistics list enabled, the first 8 bytes of input data re reserved, with each bit indicating whether that device is online.

    2. Can the gateway map multiple input/output assemblies from a single device? (e.g., E300: Assembly 100 and 101)

    • No - it is only possible to configure one Assembly in each direction for each Adapter, one Input and one Output.

    3. Is there a way to diagnose or simulate the data exchanged between the gateway and Scanner-side devices, before going online with the PLC?

    4. When connecting multiple devices through a switch to the Scanner port, does the gateway automatically detect them? Or do I need to manually define each IP and I/O assembly?

    • You'll need to manually define the IP address and connection points for each device. As long as the devices are in the same subnet and there's a path between them, it won't matter if they need to route through a switch, or if there is other traffic on that network segment.

    Hope that helps someone else as well.

    Siobhan

     