Modbus Client PLC to Profinet PLC via Gateway

Comments

2 comments

  • Hugh Whitefur

    No, this wouldn't work as the ABC3213 has a PROFINET device (slave) interface. The Wago PLC would need to have the ABC3213 added as a module via its GSD file, and then the program would need to be adjusted to read/write to the gateway. We don't currently have any gateways with PROFINET controller interfaces that would work for this application. Are there any other protocols that the Wago PLC is using to expose its data?

    0
  • Trevor Greenaway

    Thanks for clarifying. I kind of figured the ABC3213 was a slave interface and would require it to be added to the PLC via GSD. Physically the PLC also appears to have Ethernet/IP and Modbus/TCP however the manufacturer has not set it up to integrate using those protocols, so that won't be an option.

    0