Get tags from plc (s7-1500)
Hi.
I would to know if, is it possible to get tags from Siemens S7-1500 to ewon flexy 205, with symbolic directionality?. And know how.
Thanks.
-
Hi Jairo,
You should be able to read tags from an S7-1500, but what do you mean by symbolic directionality?
0 -
Hi.
There is two ways to direct tags in s7-1500 and s7-1200.
Symbolic direction : Motor 1; Motor 2; Motor 3:
Absolute direction: Db2.dbx1.0; db2.dbx1.1; Db2.dbx1.3:0 -
Hi Jairo,
From what I've seen looking through the documentation it seems like you're able to poll tags but you need to follow the restrictions on page 19 in this doc
aug-048-0-en-polling_data_registers_from_siemens_plcs.pdf
It looks like you also need to make sure that you make sure that there's a setting checked in TIA on the bottom of this link:
0 -
is the check box the Put/Get security?
0 -
You need to allow access with PUT/GET in TIA Portal in the "General" tab, under "Protection & Security > Connection mechanisms".
aug-0048-00-poll-data-from-siemens-plc-using-ethernet-protocol.pdf
Also, here is Siemens doc which explains how to do this (see page 9 - 10):
82212115_s7_communication_s7-1500_en.pdf
0 -
No is not possible; you must use DB non optimized, only direct memory access like in the S7-300;
for the future, probably siemens remove the put/get option from the s7-1500, so you can access only via opc-ua client.it's time to think to develop in ewon a io-server native for the S7-1500 :
0