Can not establish Profinet connection - ABC3213-A

评论

1 条评论

  • Siobhan Chapman

    Hi Peter

    I see my colleague local to you is working with you on this problem via our ticketing system.

    The advice with this gateway is to get the Modbus TCP Client reading the data first and then when the IO sizes are known the PROFINET configuration can be created to match those.

    Please continue to work with the support ticket to find the resolution - I see that you have some Modbus TCP data but it is not yet in the addresses you expect. Maybe you need to start reading at a different register starting address - I always suggest starting at least one register lower than documented if it is not clear whether the first register is 1 or 0. The Communicator does not adjust for "PLC numbering".

    Thanks