跳到主内容

X-Gateway Ethercat to Modbus TCP with Kuka robot and Beckhoff EK1100

评论

5 条评论

  • Kyle Reynolds

    Hi,

    What are the errors that you are getting after installing the ESI file for the Anybus? Can you share any screen shots or documenation from Kuka?

    I think the best resource for interfacing with the Beckhoff would be here but you will also want to read Network Guide - EtherCAT Slave document and other resources found on the Product Page.

    This is the pinout for EtherCAT on RJ45:
    image

    Kyle

    0
  • Alexander

    Kyle,

    Thanks for the pointers. I'm still running into some issues " help would be appreciated.

    Kuka configuration:

    We have the Anybus powered, and an Ethernet connection from an EK1100 output located in the robot controller to the EtherCAT input on the Anybus.

    I tried importing the ESI file provided on the website and adding it to the Kuka configuration as we installed it. This does not error, but upon uploading this configuration we get an error which says: "Ethercat device: Anybus X-gateway " Slave cannot be started" and "Error on reading/writing X-44" (an EtherCAT comm error).

    The ESI version from the website appears to be 29.3. Version in the ESI is #x00010009 .

    Anybus configuration:

    When I plug an Ethernet from the Modbus TCP side to the computer, I am able to go to the Anybus webpage and have configured the IP address.

    The EtherCAT slave version from the Anybus device page is software version 2.04, bootloader version 2.00. The Application version for the gateway is 3.29.

    I tried following the documentation that you pointed to (the TwinCAT system manager guide), but was unable to configure the network card in the computer (network card is Realtek PCIe FE Family Controller) and got the error "Failed to install TwinCAT RT-Ethernet Intermediate Driver" on the PC I was using. This is in step 4.1.

    My understanding is that this software is used to configure the I/O and generate an ESI XML file, which we should be able to upload to our robot configuration, I believe.

    Thanks,

    Alex Kearns

    0
  • Kyle Reynolds

    This error, what are you getting it from, the Kuka WorkVisual software?

    Does the software allow you to download the process data object (PDO) from the gateway?

    0
  • Kyle Reynolds

    Try this file:

    ABXS_ECT_V_3_22_Fixed_PDO_256bytes_for_OMRON_1.xml (116.9 KB)

    0
  • Benoit1

    Good morning,
    I have exactly the same configuration to achieve as the post above. I need to connect a kuka ethercat robot to the modbus network (telemecanique automaton) the product recommended to me is an anybus AB7901 gateway in the new ABC4016 version. By reading this post, I understand that "Alexandre" had a problem with the XML file. Do you know if his problem has been solved? So that I don't have the same problem.
    Thanks in advance.

    0

请先登录再写评论。