跳到主内容

Pulling data from siemens im151-8 pn/dp cpu

评论

14 条评论

  • Kyle Reynolds

    Hi Charles,

    That device is based on the s7-300 so you should use that IO server. You can pull data from the current connection. See the following link for documentation and examples:

    https://websupport.ewon.biz/support/product/s7300-s7400-s71200-s71500-and-vipa-0/s7-300-s7-400-s7-1200-s7-1500-vipa

    Kyle

    0
  • Charles_UAS

    hi, Kyle. I got it worked under s73400. but havent read those links. I will.
    thanks for help

    0
  • Charles_UAS

    sometime while I am on the flexy config window, the window just closes then ie stops, cant open that screen again. randomly happens, why?

    0
  • Charles_UAS

    is there any solid way to do this when you are local, rather than always over the cloud even you are in local?

    0
  • Kyle Reynolds

    Hi Charles,

    Which page of the Flexy configuration UI do you have open when this happens? I would need to see the browser logs to tell you why it happened.

    Firefox and Chrome tend to work better with the web UI in general, so I recommend trying one of those to see if you still have the problem.

    Kyle

    0
  • Kyle Reynolds

    If you are local to the device you can connect from the LAN side using the LAN IP address, or you can connect from the WAN (plant network) if you are using that for internet access (not cellular) and disable the firewall, but this is generally not recommended for security reasons.

    0
  • Charles_UAS

    I will try to capture it next time when it happens

    0
  • Charles_UAS

    agree, that makes sense, using LAN port to pin that subnet address. I was thinking to use subnet address over the cloud, it opens, but it would be the same thing if I lost the cloud.
    thanks, Kyle

    0
  • Charles_UAS


    I checked the logs, it actually shows disconnected. it is a cell type but the fallback to cable is enabled and plugged in. cable internet is good as well as 4G signals.
    0
  • Charles_UAS


    captured this one, it happens during pulling the data logs
    0
  • Kyle Reynolds

    It looks like those are happening when the cellular signal refreshes. By default, it happens every hour, but you can change that. I personally don't think it's necessary to do so often so usually change to twice a day. Go into Setup > System > Storage > Edit COM cfg and search for "MaxCallDur' and change that from 60 minutes to something higher like 720 or 1440.

    0
  • Charles_UAS

    will try it. by the way, the FALLBACK function wouldn't help to maintain the connection in this case?

    0
  • Kyle Reynolds

    The connection is only going down for a matter of seconds, however, the web server which you are interacting with at the time may take longer to come back up. So it's just not a long enough disconnect for it fail over.

    0
  • Charles_UAS

    increasing maxcell time seems making the connection more stable, thanks.

    0

请先登录再写评论。