跳到主内容

Disable WAN with Digital Input

评论

1 条评论

  • hms_support

    @Ryan_Nordhus

    Cosy 141 - DI / DO

    To configure the digital input, you can do this through the internet wizard as seen by our getting started video step 2 (180 seconds): https://youtu.be/viQR6U2qMHU?t=180

    The digital output for the cosy 141 is limited to the VPN tunnel only as seen by our manual on page 10:

    ig-0010-00-en-ewon-cosy-141.pdf

     
     

     

    image
     

    When the VPN tunnel is established then the digital output will be in an ON state. This is still a good check on whether you have internet because the eWON will disconnect/connect from the VPN tunnel if the WAN connection is disconnected / connected as well.

    eWON CD/Flexy DI/DO

    In the eWON CD / Flexy device, you'll have to use scripting to achieve these results.
    First, you'll need to create an "EWON' tag under tag setup for your digital input and digital output in your eWON CD.

    DI tag address = DI1
    DO tag address = DO1

    Lets say we name our tags the following:
    Switch (the digital input tag address)
    Digital_Output (the digital output tag address)

     

    image
     

    Once the tags are created, we can now use BASIC scripting in the eWON CD to enable your modem connection based on the digital input

    In the Init Section :
    ONCHANGE "Switch","goto DoSwitch"
    
    
    DoSwitch:
    If (Switch@<>0) Then
    rem Open Internet connection
    Setsys COM,"load"
    Setsys COM,"WANCnx","1"
    Setsys COM,"WANPermCnx","1"
    Setsys COM,"save"
    Print Time$;" Connection opened"
    Digital_Output@ = 1
    else
    rem Close Internet connection
    Setsys COM,"load"
    Setsys COM,"WANCnx","0"
    Setsys COM,"save"
    Print Time$;" Connection closed"
    Digital_Output@ = 0
    endif
    

    The instructions to limit a WAN or VPN connection via a Digital input on the eWON that I described above are located in the document below, however I did edit the WANCNX parameter for a modem connection and added a digital output tag as described:

    kb-0015-00-en-switch-to-enable-wan-or-vpn-connection.pdf

     
     

     

     

    1

请先登录再写评论。