Ewon Flexy with Micro 850
I would like to know if it is possible to read the values of a Micro 850 CPU for Ethernet communication. How is done?
-
@alexandre.freitas
Yes, the flexy is compatible with a Micro 850. You can poll tags using modbus in the Flexy.
We have a step by step guide on how to setup modbus RTU & Ethernet polling, located here:
aug-0059-00-poll-data-from-plc-using-modbus-tcp.pdf
See Q: I'm unable to use the Ethernet IP of my Micro 8xx Rockwell PLC to connect to my Flexy. on the FAQ page for info on how to enable modbus in Connected components.
https://www.ewon.biz/technical-support/resources/faq?ordercode=Flexy20500_00MA
For more information about which products we support, you can visit the flexy's PLC area on our site:
https://www.ewon.biz/technical-support/pages/data-acquisition/allen-bradley-rockwell?ordercode=Flexy20500_00MA0 -
Thanks for the feedback.
Ewon and CLP are already installed and unfortunately the Micro Logix memory mapping has not been configured. The only solution is to update the CLP program to do this reading right?
0 -
Hi @alexandre.freitas,
If the PLC doen't have the modbus mapping then you will more then likely need to download the config again.
Deryck