I am having difficulties seeing a Panelview Plus 7 HMI behind a Cosy.
Cosy is set as gateway (172.16.1.254)
Panelview (172.16.1.72) is visible to ping from the remote computer and I can remotely access the panel via its remove viewer (VNC Viewer).
I can see the HMI in RsLinx with the ETH driver, but it doesn't show up in the Transfer Utility (9.00 Rockwell). Since RsView uses Rslinx Enterprise (5.9.00) any Ideas?
-
@mareimers
In order to establish this connection you need to add the device explicitly inside of FactoryTalk View Studio. Once inside of View Studio, you will want to navigate to the connection settings and explicitly add your PanelView into the connection.
0 -
Can you point me to a place that has the procedure to do this. I am not
having luck finding how to do accomplish this.0 -
@mareimers
Glad it is working for you!
Please let us know if you have any further isuses.
0 -
Found it: It is not in the Factorytalk studio. It is in the factorytalk control console. Finally works: Thank you
0