Modbus IO Server Modbus TCP Port configuration to when EWON is Modbus Client
I want to read data from PLC thru MODBUS TCP/IP. PLC is configured with TCP port 503 for MODBUS. When I update EWON IO Server Global settings to configure TCP Port as 503 and restarted EWON. Still I have same issue.
EWon Firmware is 14.3S0. The EWON IO Server Global settings page in this firmware revision is not same as explained in the IO server document
-
Hi @Tim_hms,
Ewon LAN IP is 192.168.0.101
PLC IP is 192.168.0.1, PLC is pinging and when I try, I am able to pole data using S73&400 IO server. But I have to use MODBUS here.The "Disable Tags in Error" is not selected.
I have tried with Modbus simulator, when I set Modbus simulator port to 502 and Modbus TCP Port in EWON IO servers global setting is 503, still I am able to pole data. Strange !. But when I make Modbus simulator port to 503, Ewon stops polling data.
Other question, In my Ewon IO server global setting page, I have only MODBUS TCP PORT entry and not for other TCP Ports (EthernetIP, ISOTCP, FINS) as shown in your shared image. Is it related to firmware ?
0 -
Adding this seemed to fix it
0 -
Yes, the data is polling now. Thank you.
Is this advanced parameter "TcpPort:503" is applicable to all Flexy series and firmware versions ?
0 -
It should be available in all of the Flexy devices. I'm not quite sure what firmware this was first included in, but I believe this feature has been available for a while. I think anything in the 12,13, or 14 should include this at the very least.