Add On Profile Crashing Studio 5000 Logix Desgner

Comentários

9 comentários

  • support

    We have not encountered this exact issue, however I would suggest uninstalling and reinstalling the AOP. This is how you can reinstall it,

    1. Navigate to this directory "C:\Program Files (x86)\Rockwell Software\RSLogix 5000\Module Profiles\Install"

    2. Hit Shift + right click and select "open command window here". This does not run in powershell. If powershell is your default terminal you might need to launch terminal then navigate to the folder manually.

    3. In the command prompt type "MPSETUP/CU"

    1. A dialogue window will appear, hit next and then select "Uninstall" and select next again.

    2. From here find the "HMS Ethernet_IP Linking Device" option. PLEASE NOTE: be careful not to unintentionally uninstall any other Rockwell profiles.
      image

    3. Select Next again and then finally uninstall

    4. After the uninstall is complete please go to the following link to download and install the latest AOP software.

    https://www.anybus.com/docs/librariesprovider7/default-document-library/firmware-software/hms-aop-en2xx-r.zip?sfvrsn=bedabfd6_20

    0
  • trevor_hms

    Hi Nick,

    I followed your procedure to uninstall and re-install the AOPs. Unfortunately, I am still getting the same error after doing this. The error is repeatable and it does not occur with either of the Modbus-TCP or Serial Linking Devices. Also, I tried this with RSLogix 5000 (also installed on my VM) and I get the same error and crash.

    image

    Any other ideas about what I can try next?

    Thanks!
    Trevor

    0
  • support

    Have you ever been able to launch the configuration interface? Or has it given this message from the very beginning?

    You are plugged into the X1 ports on the front, correct?

    0
  • trevor_hms

    I have never been able to launch the configuration interface. This has occurred since my first attempt.

    Yep plugged into X1.1. Also tried X1.2.

    Ethernet port on VM is set 192.168.150.12
    Ethernet port on Host PC is 192.168.150.13
    ControlLogix Ethernet is 192.168.150.100
    Linking Device is at 192.168.150.171
    (all fixed IP addresses)

    I can ping both the ControlLogix and the Linking Device from the VM and from the Host.

    0
  • support

    I have informed a support colleague in Sweden of this behavior. I am going to update him and ask him his thoughts.

    0
  • Maribel Cassens

    Hi Trevor,

    Have you tried launching the AOP while disconnected from the Gateway? Does it give you the same error?

    0
  • support

    Hello,

    This did turn out to be a known issue, Trevor found the following.

    "The IP address for my Linking Device was 192.168.150.171. I tried changing it to something completely different (10.10.0.99) and it die NOT crash. I tried 192.168.150.170 and it crashed. I tried 192.168.150.66 and it did NOT crash! I tried several 2-digit values for the fourth octet and no crashing. However, I tried several 3-digit numbers in the last octet and it crashes. "

    This is a bug relating to the last octet of the IP address, this issue is being addressed by development.

    0
  • jakes81

    Hi Guys Has this issue been resolved yet

    0
  • support

    Hello,

    Yes, this will have been addressed in the new versions being released.

    Nick

    0