Pular para o conteúdo principal

Cannot connect to siemens HMI through eWon Flexy

Comentários

5 comentários

  • jseanor

    @Confused

    By default you are only able to download to the ComfortPanel HMIs. In order to locate the HMI, TIA portal uses a combination of an ARP message and a Siemens specific protocol (PN-DCP). Neither of the previously mentioned protocols are routeable and are only usable locally.

    Now this will not stop you from downloading to the HMI as that should work just fine.

    If you would like to go online with the HMI however a newer feature in the eWON may be able to make this happen. In firmware revision 11.0 we introduced a broadcast forwarding option. Basically this will allow the broadcast messaging to go through the VPN tunnel allowing you to auto-discover your devices and go online.

    See pages 7-8 in the below document for setup.

    aug-0070-00-en-plc-discovery-through-talk2m.pdf

     
     

     

     

    0
  • Confused

    Thank you Jordan for your reply, how do I turn on broadcast
    forwarding on the Flexy firmware version 13?

    0
  • jseanor

    @Confused

    It is quite easy to enable.

    First and foremost, ensure to follow the eCatcher setup information found in that PDF I linked previously. As for the Flexy simply do the following:

     

    1. Load the eWON webpage

    2. Select Setup from the left

    3. Select System -> Storage -> Tabular Edition -> Edit COM Cfg

    4. In the searchbar enter: BroadcastForwarder

    5. Update the value to a 1 and save the value.

    6. Reboot your device.

     

     

    flbroad
     

     

     

    0
  • prololik
     
    jseanor:

    @Confused

    It is quite easy to enable.

    First and foremost, ensure to follow the eCatcher setup information found in that PDF I linked previously. As for the Flexy simply do the following:


    1. Load the eWON webpage

    2. Select Setup from the left

    3. Select System Storage Tabular Edition Edit COM Cfg

    4. In the searchbar enter: BroadcastForwarder

    5. Update the value to a 1 and save the value.

    6. Reboot your device.


    flbroad

    Hello, @jseanor.
    I have the same problem with loading project to HMI throeugh VPN. Do you have any similar solutions for EWON 2005CD? I've checked its settings and there is no "BroadcastForwarder" item in proper section:

     

     

     

     

    0
  • Deryck Beliveau

    The broadcast forwarding feature is only available on the ewon Cosy 131 and Flexy devices.

    0

Por favor, entrar para comentar.