Comentários

1 comentário

  • Deryck Beliveau

    Hello @Nanovac,

    The configuration on the linking device does not match the one save to the module definition. You need to open the Configuration manager and make sure you download to the linking device. Then exit the configuration manager saving it to the project and definition. You also need to make sure you apply the changes.

    Deryck