EN2MB-R setup issues 8/12

コメント

17件のコメント

  • Deryck Beliveau

    Hi,

    I pulled this into a new topic as it look unrelated to the AOP. This sounds like an issue with your connection to the device. I have seen similar results when I had another device on the network using the same IP address.

    If you disconnect it from the network and then connect your PC directly to it do you still see these issues?

    Deryck

    0
  • pmccutcheon

    I'm not even at the point of going online

    I thought I was supposed to enter some kind of config offline first

     

     

    0
  • pmccutcheon

    I tried another laptop

    I get the exact same issue with the AUTHENTICATIOn question

    0
  • pmccutcheon

    I am not even attempting to go online with the unit at this point.
    I am trying to make an offline edit, configuration editor is empty.

    0
  • pmccutcheon

    it was totally unclear to me that I had to be online with the gateway (!)

    you need to:
    -have the gateway powered up
    -use BOOTP to set the address of the gateway
    -probably check in RSLINX that it can "see" the device
    -in RSLogix5000/Studio5000 not be online with the PLC
    -then click the button

    0
  • pmccutcheon

    Couple issues still unclear to me:

    -on the side of the unit it says "MAC X2" with the MAC ID --> I would guess this is talking about X2, the bottom connections
    -when I run BOOTP, I get this MAC from the FRONT connectors (X1.1 or X1.2) not from X2
    -I did manage to use BOOTP to set the X1 (Ethernet/ip) address but the note seems mixed up

    1. How does the IP on the MODBUS side get set?
      I thought it was thru the pseudo webpage (section 7.3.2 page 42) in manual?[/img][/img]
      but I could NOT set anything : couldn't type in the little box

    2. Some of the dialog boxes were malformed, I couldn't see the YES or NO buttons
      I can see the top of the buttons, but not the text
      When I clicked on the buttons anyways, nothing happened
      I could see the button border change color (expected) but no action seemed to occur
      EClipboard03

    3. One dialog not matching the manual
      ~?how do I attach an image on this webpage, cant figure it out~

    0
  • pmccutcheon


    this is the "clipped dialog box" issue
    pretty awkward, I can't tell what's going on, really blind here
    0
  • pmccutcheon

    EClipboard01 EClipboard02
    this one seems minor for now, dialog box actual not matching manual version

    0
  • pmccutcheon

    Setting the IP address on the MODBUS side

    was unable to set here : is there a trick?

    If I am supposed to use BOOTP : then the unit only lists ONE MAC address on the side : which seemed to work for the ETHERNET/IP side : very unclear what is MAC for the MODBUS side

    am a bit stuck at this point right now

    also not sure what to put in as router address if not using router

    0
  • pmccutcheon

    okay, solved the "setting the Modbus side IP address issue" - pretty easy - just turn off DHCP in the dialog box - this allows the IP address to be set

    0
  • pmccutcheon

    re the MAC ID issue:
    -the text on the label of the unit says MAC X2 but I am positive it is for the Ethernet/IP side, which I would have said is network ONE (not 2)

    -to get the MAC of the MODBUS side " it's displayed on the "home" page of the MAC%20ID%20side%20of%20unit MAC%20ID

    0
  • pmccutcheon

    so the "unreadable dialog boxes" is my main concern right now

    0
  • Deryck Beliveau

    Hello @pmccutcheon,

    The configuration does have to be done online with the Linking device but offline with the PLC.

    The MAC ID can be found from within the configuration page of the device. It looks like this is a production issue where they are printing the MAC label as "X2" when they are really providing the X1 interface MAC.

    With DHCP enabled it will prevent a static IP from being set. You can also use our IPconfig tool to set the ip address. As for the modbus side this is going to be configured thought the Modbus configuration page.

    If you would like we can discuss this further over the phone. Please give me a call at 312-893-5636 or provide me a number and I will give you a call.

     

     

     

     

     

     

    0
  • pmccutcheon

    Hello Deryck

    Attached are my notes on the setup.

    Maybe some areas for small improvements in the manual

    Unit seems to be working

    (now have to deal with the 3rd party guy on the other end :wink:

    HMS EN2MB-R Gateway Notes.docx (1.31 MB)

    0
  • pmccutcheon

    I've been a bit picky, but it's a well packaged unit, well integrated in A-B, the documentation is pretty good, and it seems to be working

    0
  • Deryck Beliveau

    Hi @pmccutcheon,

    Thanks for the follow up. You make some good suggestions that I will forward to the product manager.

    I have already reported a few like the dialog box to them already and hope to see that corrected in the next update.

    Deryck

     

     

    0
  • mitchell.hein

    A nice white paper with good details, but it did miss one thing concerning the "malformed dialog boxes"

    If you are editing your transactions, you cannot use the pulldown arrow to change them.
    For Transaction type, Endian, and int16/int32, you need to click to click twice to the right of the arrow and then once in the field itself (left of the arrow) to highlight the whole thing in blue: and then you must use the cursor keys to move through the choices. The pulldown menus do not work.

    0