Ewon Flexy 205 Tag Issues

コメント

10件のコメント

  • Tim Beaulieu

    The Disable tags in error will make it so that if it's an individual tag with a fault that it will stop trying to repeatedly call that tag. The repeated calling of a faulted tag could cause other tags to show up as faults due to the delay caused by the actual faulted tags.

    For the tags that didn't have the bad status disappear after disabling this, check and make sure that the way you are calling the tags is correct.

    As for tags not saving after you make changes this seems like a bigger issue. Do you know if you have the most recent firmware installed on the device?

    0
  • maravidis

    Hi Tim,

    Is there an easy way to check the firmware version of the device? Under system information it shows the device as "Flexy (FLEXY20500_00)"

    0
  • Tim Beaulieu

    This can be found in eBuddy when connected to the device.

    The newer firmwares it can be found down near the bottom of the page

    0
  • maravidis

    Gotcha. Here's the firmware version: 13.2s0PR

    0
  • Tim Beaulieu

    Are you grabbing data from more than one PLC or are some of the tags on one PLC working and some aren't

    0
  • maravidis

    Just 1 PLC. I'd say 90% of the tags or so are working, these are not. Seems like the Boolean ones aren't working, but all of my real number tags are now working. Maybe there's something wrong in the config for them?

    0
  • Tim Beaulieu

    Are any of the boolean tags working or is it just a certain group of them? How often are these tag values updating as well?

    0
  • maravidis

    Some other Boolean tags work. There ones that aren't are all the ones from the same "word." I wonder if there's something different I need to do on the PLC side? Also, the flexy is on autorefresh @ a rate of 1 second.

    0
  • Tim Beaulieu

    I'm just wondering if maybe there's something wrong with the address. If you take one of the working tags and try to change it to the address of one of the ones that's not working, I wonder if that will work?

    0
  • maravidis

    Looks like it. If I change the address to a working one, it works. Tried it on 2 different tags. Going to look into the PLC configuration. Thanks.

    0