Aller au contenu principal

Ewon Cosy 131 unable to see devices

Commentaires

5 commentaires

  • Kyle Reynolds

    Any LAN devices you are trying to connect to need to be on the Ewon's LAN subnet and have their default gateway set to be the Ewon's LAN address.

    Also, EthGW is the Ewon's WAN gateway, so it should be on the 192.168.x.x network.

    0
  • AmandaF

    The customer did the setup wizard and was able to see akmost all of the devices. Please see their comments below.

    I rerun setup wizard, which assigned LAN side gateway of eWON to 192.168.2.1. I accepted that, before I changed it to 172.27.5.1 which is a gateway on my switch network. I can connect now to all devices except one. Is located in vlan
    11 on my routing swtch (172.27.5.1). I can't create NAT on this switch since is configured as routing switch. Device address 192.168.1.50, vlan IP is 192.168.1.1.

    Thanks

    image001.png

    image002.jpg

    0
  • Kyle Reynolds

    The customer needs to understand that the Ewon is the gateway on the LAN (172.27.5.10). There is no setting to change the LAN gateway. The setting "EthGW" is the WAN gateway address. (The setting is ignored if they're using DHCP)

    I don't think they will be able to reach the last device you are referring to without using NAT.

    0
  • AmandaF

    Okay thank you for your help!

    Thanks

    image001.png

    image002.jpg

    0
  • Kyle Reynolds

    You're welcome.

    One more thing that they can try:

    -add a route on the eCatcher PC to reach the device network
    
    -add a route in the ewon in the static route table to reach the device network
    0

Vous devez vous connecter pour laisser un commentaire.