Allenbradley controlnet to ethernet gateway help

Commentaires

5 commentaires

  • Kyle Reynolds

    Are you aware that you are using the Eth/IP Scanner device (master) instead of the Eth/IP Adapter (slave)?

    What Controlnet devices are you connecting to? AB7673-F is typically used to map Eth/IP slave devices to a Controlnet control system.

    0
  • mathewcox

    thanks for the reply.
    im aware that is a scanner.
    this is just the unit our supplier told us we needed.

    all we need to do is map 1 bank of point io on controlnet to an Ethernet ip processor.
    the point io consists of
    1 x 1734-acnr
    1 x 1734-ib8
    1 x 1734-ob8
    1 x 1734ie2c

    it sounds like we have been sold the wrong item

    does that sound right?
    what do we actually need?

    0
  • Kyle Reynolds

    You are going to want the Ethernet/IP Adapter (slave) in order to map the IO to an EIP controller. See the AB7834.

    But, if you are in Australia as your IP shows, I would recommend also opening a case in our ticketing system (https://mysupport.hms.se), which will get you in touch with your local office. HMS.how is operated by the Americas region, so you'll need to contact your local support office in order to work with your distributor.

    0
  • mathewcox

    thanks.
    the slave option looks like what we want on the Ethernet side.

    but however.

    can the controlnet side map io data from point io to the gateway then to the plc with out a controlnet scanner in the system?
    we will only have 1 x point io bank and the gateway on the controlnet network. there is no scanner.

    0
  • Kyle Reynolds

    You would need a ControlNet scanner to pull data from the IO, which unfortunately, we don't offer.

    0