Multiple plc's connected to profinet io device
@anonouwprakj
Hi Kamaesh,
I will look into how you can connect 2 plc's to the profinet side and reach back out.
Here is the document we have for adding just one plc.
Deryck
-
Hello Kemaesh,
After talking to my colleagues, the profinet IO connection only supports 1 connection. You would need to have just one device connect to it then sync the data between the two plc's themselves.
Another possible option, if you have a newer Siemens plc, would be to use a modbus TCP gateway and have the plc's exchange data with modbus. Newer Siemens plc's support being both a modbus tcp server and client. Depending on how you want to configure the plc's modbus you would need our modbus tcp master (AB9006) or the modbus tcp slave gateway( AB7632).
Deryck
0 -
Hi Deryck, Did we get any solution to my problem?
Kaamesh
0 -
Hello Kamaish,
As mentioned in my last response we can only have one profinet master connected to the device at a time.
Deryck