AB7629-F Modbus TCP/IP Slave to Profibus Master
Dear All Community,
Please help me regarding AB7629-F Modbus TCP/IP Slave to Profibus Master Address Mapping. Right now I am using Profibus Slave Device EX600-8pPR1A.
SLOT1-16DI, SLOT2-16DI, SLOT3-16DI, SLOT4-32DO
-
Hi Fateh,
Thanks for reaching out to us.
If you're having trouble finding the correct setup for your Slave Device, you can try using the Automatic Scan functionality.
You need to be connected to the Gateway over the null modem cable, have the Profinet slave connected on the Profinet Interface, and ensure that the GSD file is already installed. After that, you can follow the scan functionality process as described in the pdf:
How to configure a PROFIBUS network with NetTool for PROFIBUS: Chapter 5 Automatic Network Scan
If this doesn't address your issue, please provide more details on which step you're struggling with. Screenshots would be helpful for us to understand your problem better. Additionally, Chapter 7 of the PDF explains how to locate diagnostic information for the Profibus Slaves you want to connect.
Best regards,
i.A. Franziska Gültig
0
Iniciar sesión para dejar un comentario.
Comentarios
1 comentario