Saltar al contenido principal

How to configure Anybus Converter EtherNet/IP adapter to EtherCAT slave for Maxon EPOS4 EtherCat to ABB OmniCore Controller Ethernet/IP

Comentarios

1 comentario

  • Siobhan Chapman

    You say:


    I would like to connect Maxon EPOS4 (EtherCAT) as a slave device

    but the Anybus Communicator is also an EtherCAT slave device so you cannot connect the two together directly, you need an EtherCAT MainDevice in the system.

    Take a look at this gateway instead:

    https://www.hms-networks.com/p/abc3107-a-anybus-communicator-ethercat-maindevice-to-ethernet-ip-adapter?tab=tab-overview

    You cannot configure the EtherCAT MainDevice in the gateway using an ESI file but if the Maxon EPOS4 responds to a scan request then the MainDevice in the Communicator gateway will add it to the scan list with the reported PDOs.

    You can download the EDS file from the gateway once it is configured for the ABB EtherNet/IP Scanner to configure that side.

    0