Connect to DirectLogic DL06
What would it take to connect a Flexy 201 to a DirctLogic DL06 plc to be able to read and write values in the plc?
We will be using port 2 on the DL06 which is a 15 pin multi function port.
Communications Port 2
Connects to HPP, DirectSOFT 5, operator
interfaces, etc.
15-pin, multifunction port, RS232C, RS422, RS485
Communication speed (baud): 300, 600, 1200,
2400, 4800, 9600, 19200, 38400
Parity: odd (default), even, none
Station Address: 1 (default)
8 data bits
1 start, 1 stop bit
Asynchronous, half-duplex, DTE
Protocol (auto-select): K-sequence (slave only),
DirectNET (master/slave), MODBUS (master/slave),
non-sequence/print/ASCII in/out
Can we use the 201 base with the FLA 3301 serial expansion card?
-
@tedsch
You should be able to use Modbus RTU over RS485 or RS422 to communicate with the Flexy using the FLA3301 serial extension card.
We also have a document related to this PLC's Directsoft software but it's for an ethernet connection. I thought it may be helpful though as the path should be similar for serial in the software.
eWON_QuickGuide_DSLaunch_Timeout_Settings.pdf (349.0 KB)
edit - you can also use RS232, and the eWON supports both full & half duplex.
0 -
I just noticed you did not say anything about being able to use RS232 for the connection. Why is that?
Also can the FLA3301 card do both full and half duplex?
0 -
@tedsch
RS232 is also supported, and we support full and half duplex.
I'd take a look the FLA3301 extension card manual for additional details regarding the extension card as well as it may help with future questions:
ig-0016-00-en-fla-3301-2-serial-ports-extension-card.pdf
7.30 MB
0 -
The manual is a bit fuzzy when it comes to full and half duplex: