    Hi!

    in the ticket this was the result:

    We noticed that the problem occurs when the AC Setpoint is calculated lower than the minimum Set point accepted by the Fujitsu. This is due to the Ambient temperature sensors reading difference. (The AC and KNX sensor.) 
     

    in normal conditions, the difference will not be that high. 