    Dear Sebastian,

    The maximal CAN bus length for the CAN baud rate 250kBd is about 280m.
    The CAN-CR200 works real-time transparent bit-wise and
    can be used for the galvanic isolation, signal improvement, splitting of the capacitive load,
    making possible star topology but it reduces the maximal CAN bus length by 40meters.

                  111m           (40m)           114m         
    [R]-------+---...---+---[R]CAN-CR200[R]---+---...---+[R]  
    Node1   Node2     Node12                 Node13   Node25  

    So the CAN bus length is almost on limit (111m + 40m + 114m = 265m).

    If there are CAN-Error-Frames even with the 500ns lock time, then
    I would recommend the use of a CANbridge NT 200 instead of the CAN-CR200.
    The CANbridge NT 200 works message-wise and extends (doubles) the maximal CAN bus length.

    Best regards
    Andreas