Proficore ne détecte plus
Bonjour,
lorsque je lance Profitrace, le boitier Proficore est bien connecté, cependant lorsque je lance un scan, il ne détecte aucune station Profibus (LiveList), j'ai testé les câbles et le réseau profibus avec une console Siemens PGField, OK.
Cependant j'ai bien la courbe sur ScopeWare (+-3V)
Le boitier Proficore peut-il être la cause ?
Dans l'attente d'un réponse.
-
Official comment
Hello Mr. Carles,
Here are some possible reasons why nothing is showing on the Live list:
-
The device scans the bus for the Baudrate, but it wasn’t connected when the system started, so it couldn’t detect the Baudrate. Alternatively, the Baudrate might have been manually set incorrectly.
-> Solution: Manually set the correct Baudrate. -
There are devices (a Master and Slaves), but they haven’t been commissioned yet. The device can only detect devices that are already configured to connect to the Master. -> Solution: Commission the Devices (using the gsd Files and set up a running Profibus System)
-
The Proficore might be plugged into the wrong port, where there is no Profibus communication. For example, it could be connected to the PLC programming port. It needs to be plugged into the correct Profibus line. -> Solution: Make sure you are connecting to a Part of the Profibus Network that Messages are going through.
If none of the above works:
Could you make a video of the ScopeWare? Does it show any data, or is it just a flat line? (I will turn this post into a support ticket so you can upload the video, since I believe that’s not possible here.)
It’s also possible that the small cable connecting the Proficore to the Profibus is broken. Could you try connecting the Profibus directly to the box to see if the cable is the problem? (Please check the other points first, as they might solve the issue.)
I hope this helps!
Best regards,
i.A. Franziska Gültig -
-
Good Afternoon,
I tested the Profibus cable between the ProfiCore and the PLC with a Siemens PGField console and its integrated port, the data is read over the network, so the cable works.
I then tried with the ProfiCore, the 1st test in automatic scan and the 2nd by setting the bus to 1.5Mbps (PLC configuration).
No detection of field devices while they are read with the Siemens console.
Then I opened the Scope, data is read.
I have videos from ScopeWare, how can I send them to you?
Best Regards.
0 -
Hi Carles!
Sorry for the late reply!
You should have gotten an e-mail that a Ticket was created last time i answered you.
When you open the Support Portal: https://support.hms-networks.com/hc/en-us
You can find your Tickets here:

If you answer to the Ticket in our Portal you can upload up to 50 MB i think.
br
Franziska Gültig
0
Please sign in to leave a comment.
Comments
3 comments