Netbiter EC310 to Dynagen TG410

Comments

1 comment

  • Official comment
    Franziska Gültig

    Hi Zack!

    I googled Dynagen TG410 and found some reference Manuals on Modbus & J1939. I don't know if that is what you want to connect with or if that are the only Protocolls that Product supports...

    But if you can choose between Modbus and J1939 i recommend Modbus since it is very easy once understood and we support most of it. 

    Then as you mentioned a Connector DWG 1522 Its not Ethernet or? you need to find out if that is Modbus RTU (that means serial) and whitch Serial Type: RS232 or RS485. In our Manual you can find a section on it each what is what. Since these are standardized connections any wiring example on the Net should work but in the end even with all the best wiring examples if a tests says nothing is exchanged switching the cables is always a good bet ;-D

    If that Connector is actually J1939 you would need to also go to the manual see below:

    hms-scm-1202-012.pdf

    Thats the Manual the Pins for J1939 you can find here: ("CAN")

    Chapter 2.3.1 I/O Terminal Block

    Modbus would be the following chapters:

    2.3.6 RS-485 Serial Interface (3-pin)

    2.3.7 RS-232 Serial Interface (3-pin)

    If you need further help please clarify which interface you are trying to use.

    br and a happy new year!

    i.A. Franziska Gültig

     