EN2PB-R Profibus Node Diagnostics

Comments

21 comments

  • Kyle Reynolds

    Hi Howard, 

    That does not appear to be latest firmware. The latest firmware is 1.4.03. 

    It can be downloaded from the HMS-EN2PB-R Product Page.

    There was a bug fix regarding the diagnostic data in 1.2.1.0, but I'm not sure this data gets automatically mapped to the Input data (if that is where you are looking for it).

    Please try the update and let me know what you find. If you continue to have problems, I can look into this further. In your response, please include the GSD file for the node in question. 

    Best Regards, 

    Kyle

    0
  • Howard burghdurf

    So is the Firmware the Hardware Firmware version.... and is the "Configuration Manager" part of the "Firmware"?

    0
  • Kyle Reynolds

    Can you provide the serial number so I can check which version of firmware it shipped with? 

    There are update instructions in the PDF included in the firmware file. The firmware is the hardware firmware version, not part of the configuration manager. 

    0
  • Howard burghdurf

    I am remote so I can't access the equipment...  It is pretty old (2018?)

     

    0
  • Kyle Reynolds

    Do you have someone on site that can connect to the USB port? The firmware update requires the USB connection. 

     

     

    0
  • Howard burghdurf

    I do not...   I'll be onsite Probably next Wed.  and provided I can access the equipment I could get that info.
    In the Mean time getting back to What I want...
    In the Mass Flow Controller (I sent the GSD file via e-mail)... per the Manual:

    There should be two Diagnostic Bytes as part of the DPV0 Cyclical data exchange

    Is this info ignored by the EN2PB?  If not, where will it end up (or how do I access it)

    0
  • Kyle Reynolds

    Hi Howard, 

    I did not receive the GSD file. Can you attach it to your response? If for some reason you don't want it to be public, you can create a support ticket here

    I imagine that these two bytes just need to be mapped to Input data. We should be able to figure it out with the GSD file. 

     

     

    0
  • Howard burghdurf

    How do you attach files?

    0
  • Howard burghdurf

    sent via a ticket

     

    0
  • Kyle Reynolds

    I got it. I will probably have to get back to you on Monday. Taking a quick look at it, this is all I see that can be mapped: 

     

     

    0
  • Kyle Reynolds

    Can you send the devices documentation where you got that info?

    0
  • Howard burghdurf

    sent under the Ticket

    0
  • Kyle Reynolds

    Do you have DPV1 activated under the Object Properties? 

    0
  • Kyle Reynolds

    Also make sure all the alarms are enabled under parameter assignment: 

    0
  • Kyle Reynolds

    This video has some information about reading the Diagnostics: https://youtu.be/it8e3Sd5yJA

    0
  • Howard burghdurf

    I did try to "enable Alarms" in the parameters, and also checked the DPV1 box.... 

    But that check box doesn't Un-Gray any of the other items on that Tab:

    And doesn't result in any additional "mapping" in the Module Defined Tags....
     

    0
  • Howard burghdurf

    Any Thoughts?

    0
  • Kyle Reynolds

    I'm not sure why it won't let you enable the alarms. I will escalate the case to the Anybus engineers and see if they can figure out why.

     

    0
  • Kyle Reynolds

    Hi Howard,

    You will need to contact the supplier or manufacturer of the device. If the diagnostics are part of the cyclic data, they need to provide a correct GSD file that allows you to select a module with that data. The device has a specific module for each specific cyclic I/O data, and it seems like there is no module for the cyclic diagnostics.

    0
  • Howard burghdurf

    So there is this "CIP" section in the HMS users manual:

    Can this be used to get the Diag Data via a Msg Instruction?
    Not clear on how this would be set up....
    Below is My stab at it:

    0
  • Kyle Reynolds

    Hi Howard, 

    I found another case where another customer spent a lot of time trying to get this work but was unsuccessful. 

    Essentially, this is what they found:

    > The Anybus Gateway was an HMS-EN2PB-R, the PLC was a ControlLogix with 1756-L71 (FW 30.014) processor and ENBT (FW 6.006) Ethernet IP Module and the Profibus Slave was an ABB Aztech 600 Fluoride Analyser.

    > Reading cyclic data from the connected Profibus node worked fine. But the problem was reading/writing acyclic data (Class 2) from the Profibus node.

    > We tried every feasible combination of values in a CIP message –

    > Specifically, we couldn’t get this message to work –

    But some of the other commands did work. We then using a Profitrace (Profibus DPv1 Master) to look at the Profibus messages-

    1. Successfully established PROFIBUS DPV1 communication with the ABB Analyser using our PROFITRACE.


     2. Initiated DPV1 messages from the HMS-EN2PB-R linking device using the Get_Atrribute_Single function.
    However, we've encountered a slight discrepancy in the default Send_Timeout settings. The HMS linking device has a default Send_Timeout of 1000 ms, while the PROFITRACE is set to 5000 ms.

    The ABB analyser prefers a Send_Timeout of 6960 ms, closer to our PROFITRACE setting. Due to the discrepancy with the HMS linking device's Send_Timeout, the ABB analyser aborts the communication.

    > TLDR - Essentially, it timeouts and the connection is closed.

    > We would like to try to increase the timeout on the HMS-EN2PB-R, but it was getting a bit too complicated, so we gave up. We tried with a timeout of 5000ms on our USB->Profibus to poll the Slave, and that worked.

    0