Skip to main content

ABC3013-A with S7-1200[Profinet]

Completed

Comments

1 comment

  • Official comment
    Franziska Gültig

    Hi Erik!

    An update for who might face similar cases (this was analysed in a Ticket further)

    If the Home screen shows:

    Profinet in idle Mode. The PLC is not jet in run state.

    Other issues, that could impact the Watchtable not showing anything, would be the difference between process image and periferal adresses. Depending on the PLC the process image might be very small and if the addresses assigned exceed the process image range they need to be adressed differently. 

    https://support.industry.siemens.com/cs/document/18325417/where-and-when-do-you-need-peripheral-addressing-?dti=0&lc=en-ES

    In this case the process image was big enough but it is good to keep in mind if there is trouble with the watchtable.

    br

    i.A. Franziska Gültig

Please sign in to leave a comment.