FLEXY 205 WITH MITSUBISHI QJ71E71-100
CompletedHi everyone,
i want to pooling data from Mitsubishi Q170MSCPU [basically it was integrated cpu Q03UDCPU with motion cpu] through QJ71E71-100 (ethernet module)
But i can't found option for MC protocol at parameter QJ71E71-100
Do you guys have any guide or experience for integration it?
Thank you,
best regards,
Joned
-
Hi Joned!
Please take a look at the Ewon Techforum
I found this post there:
Mitsubishi polling data (ewon.biz)
I hope that helps!
Br
i.A. Franziska Gültig
0 -
Hi Franziska,
Thank you for the link,
i will try it next week on site, i hope it can work properly
i will update here with documentation if it worksBest regards,
Joned
0 -
Update:
it works fine if I connect it from Q71E71-100
we just need to crosscheck the assignment IP of module, network number and station number
the default for MC port will be: UDP=5000/5001; TCP:5000
thank you,>here my example parameter
>here the parameter for Melsec IO server
0