FLEXY 205 WITH MITSUBISHI QJ71E71-100

Completed

Comments

3 comments

  • Franziska Gültig

    Hi Joned!

    Please take a look at the Ewon Techforum

    I found this post there: 

    Mitsubishi polling data (ewon.biz)

    I hope that helps!

    Br

    i.A. Franziska Gültig

    0
  • djoneddd

    Hi Franziska,

    Thank you for the link, 
    i will try it next week on site, i hope it can work properly
    i will update here with documentation if it works

    Best regards,

    Joned

    0
  • djoneddd

    Update:

    it works fine if I connect it from Q71E71-100
    we just need to crosscheck the assignment IP of module, network number and station number
    the default for MC port will be: UDP=5000/5001; TCP:5000
    thank you,

    >here my example parameter 

    >here the parameter for Melsec IO server

     

    0