RSlogix5000 setup ANYBUS ABC4014-A EtherNet/IP
I am setting up coms between a Siemens 1500CPU and AB 1756-L61 CPU via the ANYBUS ABC4014-A
The signal that I send are going to the Siemens CPU but I am not receiving anything on the RSLogix 5000 side.
Fault on the RSLogix side is code 16#0203 Connection timed out.
If I log into the gateway, I can see the send and receive data on the gateway. The following error is on the gateway "The received data is not valid".
The send received size is 16 bytes (SINT setup on the Allen Bradley side)
The same happens using the EDS file gateway and the generic Ethernet module when setting up the RSLOGIX5000
-1
-
Hi.
I got it working. Updated the CPU to V20 and the ENBT ethernet card firmware to V6