Flow meter scaling issue using flx3402 i/o card

Completed

Comments

2 comments

  • Official comment
    Franziska Gültig

    Resolution of the Ticket:

    Here is the calculation for your reference.
     
    The raw value is 0 to 65535 for 0 to 20mA and the theoretical raw value for 4 to 20 mA is 13107 to 65535.
     
    As per your requirement (0.8 = 4mA = 13107) & (350 = 20mA = 65535)
     
    Real Physical Conversion Value Formula
     
    When configuring a tag under the IO server in the “Setup” mode of the Tag page, a conversion can be applied such as: Y = ax + b
     
    X1 = 13107, X2 = 65535 & Y1 = 0.8 & Y2 = 350
     
    After calculated the a & b value from the below formula 
     
    a = (Y2-Y1) / (X2-X1) & b = Y2X1 - Y1X2 / (X1-X2)
     
    The final value for a = 0.0066605 & b = -86.5

    Note: This formula and conversion are available in the FLX3402 manual please download to click on this LINK.