Scan List Configuration
Hello,
I have a AB7832 Ethernet IP to Profibus X-Gateway. The Profibus side is connected to our PLC and appears to be working. The Ethernet IP side is connected to a Keyence sensor.
I cannot load Anybus's EDS file on the Keyence sensor but I can view Keyence's EDS to understand the assembly structure.
Tell me I'm wrong but I should be able to change the Anybus Gateway's scan list to match that of the Keyence sensor, correct?
If so, I am not able to change the scan list configuration via the website user interface. The option is not available.
-
Hi,
It sounds like you have the wrong device. This Anybus unit is an Ethernet/IP adapter. If the Keyence has an EDS file it sounds like it's an adapter as well. The Anybus you have would require an Ethernet/IP scanner like a PLC to communicate with it.
The right device for this is likely a AB7671 which is Profibus slave to Ethernet/IP scanner.