Disabling Transaction(s) for EN2MB-R

Comments

1 comment

  • Official comment
    Franziska Gültig

    Hello Don!

    What is your goal behind enabling or disabling ModbusTCP transactions?

    As I understand your question you want to disable some of them but not all is that correct?

    All ModbusTCP read transactions are always 'enabled' they are run cyclically in the scan time specified you can change the scan-time to a higher number so it will be requested less often.

    If you have a ModbusTCP write transaction you can switch the Trigger to 'ON DATA CHANGE'

    And this means the Data will only be written to the ModbusTCP server if you change it from the EthernetIP side.

    https://www.anybus.com/docs/librariesprovider7/default-document-library/manuals-design-guides/hms-scm-1202-181.pdf#page=46 

    There is no Option to disable a single or several read transactions.

    But if you check the Control Status Word you could set the whole Gateway into 'Idle' if you want it to stop communicating on the Modbus TCP side.

    br

    Franziska Gültig

    Technical Services Engineer