Anybus xGateway AB7831-F in Studio5000
I have an Anybus xGateway AB7831-F that I am using as an intermediary between a National instruments cRIO 8055 and an Allen Bradley 1769-L30ER. I have successfully sent data from the cRIO to the AB PLC using the how two guide on the HMS website for this module. However when I try to write date from the AB PLC to the cRIO, the AB message block errors out with error code 16#000c and message of "Cannot perform requested service in current mode or state".
0
-
To close this out, after working with HMS support, we were able to get the EDS file working and I am able to address the module properly via tags instead of using the MSG block. I was never able to get the MSG write block to work.
1
Please sign in to leave a comment.