HMS Anybus-X-Gateway AB7670 communication with Allen Bradley 1734-AENTR/B
I'm working on a project where I use Anybus-X-Gateway AB7670-F (Ethernet IP scanner - PROFINET IO device).
I was trying to set up communication between the SIEMENS S7-1500, which is on Profinet, and several devices on the Ethernet network.
The devices located on the Ethernet are:
Allen Bradley 1734-AENTR/B, BOSCH welding case, Türck module and again Allen Bradley 1734-AENTR/B.
The problem is that I cannot establish communication with the first and last devices on the Ethernet network (Allen Bradley 1734-AENTR/B).
The connection (link) is present, but the NS light flashes green and the MS flashes red. Everything is OK on the Profinet side (green). The PLC communicates completely
normal with the remaining two devices (BOSCH and Türck).
Everything is fine on the Profinet side in the TIA portal.
Is it possible that I cannot establish communication because it is an Allen Bradley device? I don't know what I'm doing wrong.
-
There could be an issue with the connection setup with the Allen Bradly device. I would double check the size of the connection is configured correctly. You could also get a network capture between the EIP scanner and the network to see if any device is responding with an error message. This would tell you more about the connection issue.