Skip to main content

AB7000C - configuration

Comments

24 comments

  • Deryck Beliveau

    Hello Jefferson,

    Thank you for submitting a topic.

    When you configure the module in logic you just need to make sure the IO size match exactly how the size that is configured on the device.

    Right click on subnetwork in the tree and open the "subnetwork monitor" From here you will see the byte size. Make sure the combined modules sizes you add to your device match this size. You typically want to start with the larger size first then add smaller ones. In the image below I would use one 4 byte module and then a 2 byte module for input data then a single 2 byte module for the out size. If the size was 6 I would use a 4 byte and a 2 byte module.

    0
  • jivanqui

    I don´t know if helps, but the guys passed to me the table of configuration:

    0
  • jivanqui

    Ok Deryck

    Thanks for your help.

    I tried to change in plc hardware your suggestion, but not work.

    I check in subnetwork monitor like you show, and I can see that I´ve a colision at In Area, like in the picture:

    When I dismark the last Read, the colision get out, like in the picture:

    BR

    0
  • Deryck Beliveau

    you can update the response for the additional transaction to the 10th byte.

    You will also want to update the config in symatic to match the 10 bytes in and 4 bytes out. You out area should change to 12 once you move the conflict
    You should be able to use a 8 byte + 4 byte for the IN and then a single 4 byte for the OUT.
    Deryck

    0
  • jivanqui

    Ok Deryck

    I did the configuration for Data location, works well.

    I configurated the new words in plc program, but the problem coninuous

    Another suggestion?

    BR.

    Jefferson

    0
  • Deryck Beliveau

    I would expect this to work now. Did you download the configuration to the communicator?

    Is there communication on the bus? Is there any additional error messages in the diagnostic tab?

    What data did you move into the 0x400 - 0x4003? Perhaps I am overlooking something in you config. Could you share a copy for me to look over?

    Deryck

    0
  • jivanqui

    hi Deryck

    "Is there communication on the bus?" - I don´t think so, because only side profibus e pc are connect, the RS232 are disconnected. I´m working in laboratory far from the equipment.

    "Is there any additional error messages in the diagnostic tab?" Is this the diagnostic tab? Picture:
    image

    "Could you share a copy for me to look over?"

     

     

    0
  • Deryck Beliveau

    Hi @jivanqui,
    Sorry I wasn't very clear, I was referring to the profibus network not the serial side. The serial side does not need to be connected for the profibus side to have a connection. You know if your profibus network is configured correctly and if there is communication on this bus? Does the DP slave Diagnostics tab in Simatic provide any more details on the connection error.

    Can you also verify what version of Anybus Configuration Manager you are using? Have you downloaded this configuration to the Anybus Communicator?

     

     

    0
  • jivanqui

    Hy Deryck, ok sorry my mistake

    The configuration is correct in profibus network, follow in the picture of DP slave Diagnostic:

    I make download the configuration, after change the parameter location because the colision , but the configuration is the same for supplier of the equipement send for me.

    For Profibus has only configuration: Fieldbus type: PROFIBUS-DP. I think is correct, right?

    The version of ACM follow in the picture:

    0
  • Deryck Beliveau

    Based off the errors in Simantic I am wondering if you need to download to the PLC or profibus network.

    Deryck

    0
  • jivanqui

    Sorry, I didn´t undertand.
    I already download the hardware of plc. But is possible for me do this again anytime is necessary.

    0
  • Deryck Beliveau

    Is it working now or are you still seeing those errors you posted?

    0
  • jivanqui

    Still with errors

    0
  • Deryck Beliveau

    Hello @jivanqui,

    Please review the steps in the following application note and verify you are following all the steps.
    https://cdn.hms-networks.com/docs/librariesprovider7/default-document-library/application-notes/hms-sci-1204-027.zip?sfvrsn=4cecaad6_4

    Deryck

    0
  • jivanqui

    Morning Deryck,

    I did a new test: I put a remote intead gateway, make a new configuration for a new hardware, and you can see the result in pictures bellow:




    With remote, the plc works well, whithout failure.

    And now using the same plc, puting the gateway and make a configuration for the hardware:




    With gateway, the plc and gateway has failure for network profibus.

    I already try tree gsd files that has in website.

    BR

    Jefferson

    0
  • Deryck Beliveau

    @jivanqui,

    Can you describe the LED's What color are they and how are they flashing. Is LED 6 flashing green? Is led 4 off?

    Deryck

    0
  • jivanqui

    Hi Deryck

    The LEDs on the communicators are as follows:
    1 - OFF, 2 - RED, 3 - OFF, 4 - OFF, 5 - RED, 6 - GREEN flashing

    0
  • jivanqui

    Deryck

    How I can do the factory resset?

    0
  • Deryck Beliveau

    The LED's indicate that the profibus side is offline but no other errors.

    Maybe the node id is not set correctly? Double check the switches under the front cover.

    You can factory restore the device from Tools > options > module > factory restore

    Deryck

    0
  • jivanqui

    Hi Deryck

    Sorry, yesterday we have a maintenence in stop line, because this I can´t work in the problem anybus.

    The node id I adjust for 11 (eleven), but I change many times. I already change for other positions too.

    I did factory restore and download the backup again.

    The problem is the same untill now.

    I already use another cpu, like 300 series, I used another card anybus the same type.

    But, nothing solver.

    Can you send for me the gsd file?

    And more one question: Is didn´t configurate the SFC14 for collection dates, because the hardware has problem, by that I know, this is not make a difference to works in hardware, correct?

    Thank

    BR

    Jefferson

    0
  • Deryck Beliveau

    Can you try with the following configuration volume2 (1).cfg (16.0 KB)

    It looked like the mailboxes for the config could have been modified and causing issues. This one should have the restored to the default.

    Deryck

    0
  • jivanqui

    Hi Deryck

    I did the same procedure to another communicator, for humity equipement, restored to the default mailbox configuration, and works well too.

    Now I can install both anybus communicator in my system.

    Thanks too much!

    BR

    Jefferson Ivanqui

    0
  • jivanqui

    Morning Deryck

    This configuration works well now. No more problem in hardware plc siemens.

    The LEDs on the communicators are as follows:
    1 - GREEN, 2 - OFF, 3 - OFF, 4 - OFF, 5 - RED, 6 - GREEN flashing

    Now I need to wait the line stop and install for test to transfer dates of equipement to plc.

    But, I didn´t undertand with parameters you changed.

    Thank

    BR

    Jefferson

    0
  • Deryck Beliveau

    Glad to hear it is up and running.

    I restored the mailboxes for the Profibus interface. It looks like they had been edited or possibly came from a different version of the ACM software. Looking at the field bus section you should now see fieldbus specific.

    0

Please sign in to leave a comment.