Error code 16#012a invalid output application path, adding module to compactlogix 5069-L310

Comments

3 comments

  • Deryck Beliveau

    What is the article number for the anybus gateway? The error points towards the EDS file being incorrect. You can try adding it as a generic IO modules with instances input 100 output 150 config 1. Or we can see if we can find you the correct eds file from the devices support pages.

    Deryck

    0
  • WSteen

    Thanks Deryck, I managed to solve the problem, EDS file was fine but did not have the right amount of SINT's set up in the PLC software

    0
  • Deryck Beliveau

    Thanks for a follow up, I typically expect an error about the size when this is the case. Glad to hear you have it working.

    Regards,
    Deryck

    0