Zum Hauptinhalt gehen

RSlogix5000 AB9006-B EIP-Modbus TCP setup?

Kommentare

4 Kommentare

  • Kyle Reynolds

    You should be able to create the module, like below, after importing the EDS file: 

    Then you should see the data tags under 'Controller Tags':

    You could also use 8 INTs or 4 DINTs. 

     

    0
  • flemingtb

    My Module definition shows bytes instead of SINT, and it's not changeable.

    0
  • Kyle Reynolds

    That sounds like an RSLogix issue. Can you share a screenshot?

    I just added the device pictured above using RSLogix 33.12 and the EDS file from the product page (https://www.hms-networks.com/p/ab9006-b-anybus-x-gateway-modbus-tcp-client-ethernet-ip-adapter?tab=tab-support). 

     

    0
  • flemingtb

    Looks like i used the wrong EDS, the one i got form the website the first time is EDS_ABX_ETNM_2P-EIP_2P_V_1_3.eds

    DL the other one and it has all of the data tags.

    0