Zum Hauptinhalt gehen

SNMP IO Server

Kommentare

4 Kommentare

  • Kyle Reynolds

    You don't see this option? 

    Can you explain in more detail the problem you are having with it? 

     

    0
  • Santhoshkumar

    I didn't understand the syntax    After Status which address we need to put IP Or OID

    I have attached mapping table which is having Prefix And OID

    suppose  Device IP-192.168.0.9

    Give me a example for this.. I trying to know device communication status...




    0
  • Kyle Reynolds

    I believe this should be the IP address, not the OID address. The manual refers to it as the "Global Device Address": 

    See IO Servers Manual page 73. 

    See also: 

     KB-0150-00 - Publish tags in SNMP 

    KB-0156-00 - Send SNMP traps on alarm 

     

    0
  • Santhoshkumar

    I Have configured and all parameters are polling ok

    And For a Communication Status i put address  like this:

    Status,192.168.0.9   // Type Integer 

    Here no error in communication but Value always 0 //  it  should be 1

    0

Bitte melden Sie sich an, um einen Kommentar zu hinterlassen.