AB7318-B Canbus to Ethernet/IP programming
I am attempting to connect our Canbus devices to our CompactLogix. I have done the research and it shows this Communicator is the correct hardware.
I have downloaded Anybus Configuration Manager Version 1.7.1.1. When I select the "Network" page from the menu on the left and go to "Network Type" the only option for EtherNet/IP is "EtherNet/IP + Modbus - TCP"
This is different from the manuals I have downloaded and the videos I have watched. I was expecting EtherNet/IP by itself, I would rather not use Modbus.
Please advise.
-
Hello,
Modbus is supported in the event the application calls for it. You certainly do not need to use it, so you can just ignore that functionality.
Thanks!
Nick
0 -
The way it is listed I do not see an option to not use it and have Ethernet/IP. Is it just a matter of in the Modbus Addressing Mode I select Anybus Addressing and it does not use Modbus?
I uploaded the photo of what I am talking about.
0 -
If you are not using Modbus the Modbus addressing mode does not matter. Although it is listed there you can just ignore it.
Best regards,
Nick0 -
Ok thanks. The way it appears I thought it was going to force me into a Modbus addressing scheme, which would require a separate gateway since Modbus is not native to compactlogix.
Have a good day
0 -
Nope, you should be all set, you also have a good day!
Nick
0
Bitte melden Sie sich an, um einen Kommentar zu hinterlassen.

Kommentare
5 Kommentare