Connect to DirectLogic DL06

Kommentare

4 Kommentare

  • hms_support

    @tedsch

    You should be able to use Modbus RTU over RS485 or RS422 to communicate with the Flexy using the FLA3301 serial extension card.

    We also have a document related to this PLC's Directsoft software but it's for an ethernet connection. I thought it may be helpful though as the path should be similar for serial in the software.

    eWON_QuickGuide_DSLaunch_Timeout_Settings.pdf (349.0 KB)

    edit - you can also use RS232, and the eWON supports both full & half duplex.

     

    0
  • tedsch

    I just noticed you did not say anything about being able to use RS232 for the connection. Why is that?

    Also can the FLA3301 card do both full and half duplex?

    0
  • hms_support

    @tedsch

    RS232 is also supported, and we support full and half duplex.

    I'd take a look the FLA3301 extension card manual for additional details regarding the extension card as well as it may help with future questions:

    ig-0016-00-en-fla-3301-2-serial-ports-extension-card.pdf

    7.30 MB

     
     

     

     

    0
  • tedsch

    The manual is a bit fuzzy when it comes to full and half duplex:

    0