Error code 16#012a invalid output application path, adding module to compactlogix 5069-L310
Trying to add anybus IP adapter to Allen Bradley RSlogix 5000 network but keep getting the following error code "16#012a invalid output application path". Module part number is 4,044,014 using EDS file 0534000C03010109.eds with 40 SINT inputs and 40 SINT outputs?
-
What is the article number for the anybus gateway? The error points towards the EDS file being incorrect. You can try adding it as a generic IO modules with instances input 100 output 150 config 1. Or we can see if we can find you the correct eds file from the devices support pages.
Deryck
0 -
Thanks Deryck, I managed to solve the problem, EDS file was fine but did not have the right amount of SINT's set up in the PLC software
0 -
Thanks for a follow up, I typically expect an error about the size when this is the case. Glad to hear you have it working.
Regards,
Deryck0