  • Tim Beaulieu

    Hi @MD_Raja,

    What is the LAN IP address of the Ewon device and the Modbus TCP device? Is it responding to pings? Do you have disable tags in error set on the device?

     

    image
     

    -Tim

     

     

     

     

    0
  • MD_Raja

    Hi @Tim_hms,

    Ewon LAN IP is 192.168.0.101
    PLC IP is 192.168.0.1, PLC is pinging and when I try, I am able to pole data using S73&400 IO server. But I have to use MODBUS here.

    The "Disable Tags in Error" is not selected.

    I have tried with Modbus simulator, when I set Modbus simulator port to 502 and Modbus TCP Port in EWON IO servers global setting is 503, still I am able to pole data. Strange !. But when I make Modbus simulator port to 503, Ewon stops polling data.

    Other question, In my Ewon IO server global setting page, I have only MODBUS TCP PORT entry and not for other TCP Ports (EthernetIP, ISOTCP, FINS) as shown in your shared image. Is it related to firmware ?

     

     

    0
  • Tim Beaulieu

    Adding this seemed to fix it

    0
  • MD_Raja

    Yes, the data is polling now. Thank you.

    Is this advanced parameter "TcpPort:503" is applicable to all Flexy series and firmware versions ?

    0
  • Tim Beaulieu

    It should be available in all of the Flexy devices. I'm not quite sure what firmware this was first included in, but I believe this feature has been available for a while. I think anything in the 12,13, or 14 should include this at the very least.