    Hello Kemaesh,

    After talking to my colleagues, the profinet IO connection only supports 1 connection. You would need to have just one device connect to it then sync the data between the two plc's themselves.

    Another possible option, if you have a newer Siemens plc, would be to use a modbus TCP gateway and have the plc's exchange data with modbus. Newer Siemens plc's support being both a modbus tcp server and client. Depending on how you want to configure the plc's modbus you would need our modbus tcp master (AB9006) or the modbus tcp slave gateway( AB7632).

    Deryck

    0
  • anonouwprakj

    Hi Deryck, Did we get any solution to my problem?

    Kaamesh

    0
  • Deryck Beliveau

    Hello Kamaish,

    As mentioned in my last response we can only have one profinet master connected to the device at a time.

    Deryck